A: No, tenant breakers are sold separately. This allows for selection of amperage to fit the application. WP6512RJB has provisions for up to 225A for each meter position. Siemens Type QP, QPH & HQP or Murray Type MP-T, MP-HT, MP-MT are approved for 125A or less. Siemens Type QS, QSH, QSHH, HQS & HQSH are approved for up to 225A.
by|Aug 9, 2019
1 found this answer helpful
Q:can I connect 2 of these together for an 4 unit building
by|Jul 23, 2019
1 Answer
Answer This Question
A: No, Uni-PAK metering is completely self-contained, not modular. The 4-gang version would be WP4411RJ. To download the cut sheet for this device please go to the link below and select "Downloads" and enter WP4411RJB in the search box. We do offer modular solutions if you have height restrictions. Please send a request with your utility name to productselection.us@siemens.com for further guidance.
https://w3.usa.siemens.com/powerdistribution/us/en/Pages/low-medium-voltage.aspx
by|Jul 25, 2019
Q:Can I use this to provide 125 amps from 1st meter to main house and 100amps from 2nd meter to ADU/Accessory Dwelling unit ?
by|Jun 4, 2019
1 Answer
Answer This Question
A: Yes, consider Q2125 and Q2100 for the tenant main breakers.
by|Jun 4, 2019
Q:is it con ed approved for nyc?
by|Apr 15, 2019
1 Answer
Answer This Question
A: WP2211RJ is not ConEd approved. It is our understanding that currently ConEd does not allow PAK style units. Nearest approved offering would be of modular metering design. Consider WML21225RJ. This would require use of a tap box for incoming power. Consider WTB1400CU. Lugs are sold separately with options on the specification sheet. To download go to the link below and click on "Downloads" and enter the catalog number in the search box.
https://w3.usa.siemens.com/powerdistribution/us/en/Pages/low-medium-voltage.aspx
by|Apr 16, 2019
Q:is this meter bank suitable for a two family house?
by|Mar 3, 2019
2 Answers
Answer This Question
A: Yes, I used it for that suppose as well
by|May 31, 2020
A: Conceivably, yes. Please check with your utility for approval before purchase. Or please provide your state and utility name and we can check for you.
by|Mar 5, 2019
Q:If each socket can hold 125amp circuit, does that mean maximum load for this panel is 250amp?
by|Feb 20, 2019
1 Answer
Answer This Question
A: WP2211RJ has a continuous bus amperage rating of 200A. Tenant breakers can be a maximum of 125A each. 2 x 125A = 250A total, x 80% continuous to get the 200A rating.
by|Feb 21, 2019
Q:Do the meters have a bypass handle as required on Long Island
by|Feb 15, 2019
1 Answer
Answer This Question
A: No, WPL4312RJ is the lever bypass offering. Verify utility approval prior to purchase. Line side lug kits sold separately. See cut sheet for offerings. To download the cut sheet for this item go to the link below and click on "Downloads" and enter WPL4312RJ in the search box.
https://w3.usa.siemens.com/powerdistribution/us/en/Pages/low-medium-voltage.aspx
by|Feb 19, 2019
Q:Can you feed this product with 200A cable coming down from service head?
by|Feb 11, 2019
3 Answers
Answer This Question
A: No it has to be 300 amp cables 2) 500 mcm hot and 1) 300 mcm neutral.
by|May 21, 2019
A: The meters are bused for 100 amp. They make another boxes for 200 amps.
by|May 21, 2019
A: This is ultimately up to the designer/contractor but the incoming service cable should be sized to be greater than the protection. The WP3311RJB bus is protected by the 3 individual tenant breakers. These can be a maximum of 125A each. 3x125A = 375A total, x 80% continuous to get the 300A bus rating.
by|Feb 12, 2019
Q:Can I put 125 amp breaker in each
by|Jan 29, 2019
3 Answers
Answer This Question
A: Yes. WP2211RJB accepts 125A maximum for each tenant breaker. Use breaker Type QP. Consider Q2125 for 10kA interrupt rating.
by|Jan 29, 2019
A: Yes.
by|Jan 31, 2019
A: Yes, I believe that each main breaker(s) Is/are rated up to 125 Amp individually. check the following link.
https://www.homedepot.com/p/Siemens-Uni-PAK-2-Gang-125-Amp-Tenant-Main-Breaker-Meter-Socket-WP2211RJ/206109554
Since this is a Siemens most utility companies do not accept the original meter rings that comes with this unit and you have to buy what is acceptable and some modifications required. Not any main breaker would work on this unit and you either have to find a place that have them or do a special order.
Great unit for a small compact area but I wish I had bought a Square D double meter instead which one can get readily available parts.
by|Jan 31, 2019
Q:Hello,
I planned on using a 2 1/2in. hub to go into this. Will that work on this product?
Thank You!
by|Jan 28, 2019
1 Answer
Answer This Question
A: Yes, you would need to order the 2-1/2 HD type hub available as EC56855. This is listed on the wiring diagram. To download the wiring diagram go to link below and click on "Downloads" and enter WP3311* in the search box.
https://w3.usa.siemens.com/powerdistribution/us/en/Pages/low-medium-voltage.aspx